Control
of Hazardous Energy (Lock-out/Tag-out)
Part 85 MIOSHA
- Tag-out
Devices
- Lock-out
Devices
- Procedures
- General
- Plug/Cord
and Hose - connected type equipment
- Electrically
Powered Equipment
The procedures specified in this section comply with the requirements
for the isolation or control of hazardous energy sources set forth in
Part 85 or MIOSHA). The accidental release of energy during, maintenance
work can and frequently does cause severe injuries, amputations, and
death. Energy can be present in the form of electricity, potential energy
(due to gravity) stored in elevated masses, chemical corrosivity, chemical
toxicity, or pressure.
The only exceptions, allowed by MIOSHA, to these requirements are those
situations involving "hot tap" operations. For this exception to be valid,
the Hope College personnel involved must demonstrate that the continuity
of services is essential, that shutdown of the energy source is impractical,
and that documented (written) procedures and special equipment have been
implemented that will provide proven effective protection,
These procedures apply to all maintenance or installation operations
conducted at Hope College facilities.
- Tag-out Devices
Tags affixed to energy isolating devices are warning devices
that do not provide physical restraint on those devices that a
lock would provide. Any tag so attached to an energy isolating
device must not be removed without authorization of the person
attaching, it, and it must never be bypassed, ignored, or otherwise
defeated. Tags must be legible and understandable in order to be
effective. Tags must be made of materials which will withstand
environmental conditions encountered in the workplace. When utilized,
tags must be securely attached to energy isolating devices so that
they cannot be inadvertently or accidentally detached during use.
Tag-out devices must be substantial enough to prevent inadvertent
or accidental removal.
Tag-out,devices must wam against hazardous conditions if the
machine or equipmeqt is energized and must include appropriate
warnings such as:
DO NOT START
DO NOT ENERGIZE
DO NOT OPEN
DO NOT OPERATE
DO NOT CLOSE
- Lock-out Devices
Lockout devices and practices vary by nature and function.
Several effective lockout devices and practices are listed as,
follows:
- Padlocks. Key operated padlocks are recommended and should
be assigned individually,
- Multiple lock adapters will enable more than
one worker to place their own padlock on the isolating
device.to guarantee that the machine or equipment
will remain deactivated until each and every employee
completes their own task, and only then will the
last padlock beremoved.
- Chains or other commercially,
available devices should
be used to prevent valves
from being opened or, in
some cases, closed The
principle of multiple lock
adapters still applies
even when chains or other
devices are used on operations
requiring more than one
employee.
- Procedures
- General
If energy-isolating devices are not capable of being
locked out they must be modified so that they are capable
of being locked out whenever major replacement, repair,
renovation, or modification of the machine or equipment
takes place. Whenever new machines or equipment are installed,
energy-isolating devices for such machines or equipment
must be designed to accept a lockout device,
If an isolating device cannot be locked out for any
reason, then additional steps must be taken to assure
full employee protection such as removing fuses, blocking
switches, blanking off lines, etc.
If the machine or equipment is not capable of being
locked out, a tag-out procedure must be documented and
utilized. The tag-out procedure must provide full employee
protection equivalent to a lockout system, For full employee
protection, when a tag-out device is used on an energy-isolating
device, the device must be attached at the same location
that the lockout device would have been attached, and
must demonstrate that the tag-out device will provide
a level of safety that is equivalent to that of a lockout
- Plug/Cord and Hose-Connected Type Equipment
When servicing or installing plug/cord or hose connected
electrical, pneumatic, or hydraulically powered equipment,
the cord or hose shall be disconnected from the equipment
to be worked on, prior to starting the work. A tag
warning against reconnecting the plug or hose shall
be affixed to the plug or hose end,
Any stored energy (e.g., capacitor voltage, hydraulic
pressure) shall be safely released prior to the, start
of maintenance or installation work.
- Electrically Powered Equipment
Electrically powered equipment shall be de-energized
and their source of electricity manually disconnected
from them prior to the removal of protective covers
or the start of other maintenance or installation
work. It is important to recognize that locking and
tagging on/off switches is often not sufficient to
prevent accidental start up or prevent voltage from
being present in the equipment. If the equipment
is not wired properly (i.e., the polarity is reversed)
or the switch is of the single pole type, voltage,
can be present even if the operating.switch is in
the off position. For these reasons, manual disconnects
must be placed in the off position and/or the equipment's
power fuses removed from the motor control center.
The lock-out/tag-out procedure is as follows:
- Each person working, on the circuit or piece of equipment
shall place a padlock and warning tag on the electrical,
isolation device (e.g., disconnect switch).
- Each person working on the circuit or piece of equipment
shall attempt,to energize or start the piece of equipment
prior to starting work. Each on/off switch capable of energizing
the equipment must be "tried."
- If the try step reveals that the equipment
is capable of being energized, the proper disconnects must
be located
and locked out and the try step repeated.
- As each person completes his or her task, they shall remove
their padlock and tag from the energy isolating device.
- All protective covers or panels shall
be securely re-attached prior to energizing the equipment
after work is.completed. In the event that protective covers
must be removed to make adjustments on energized equipment,
appropriate guards must be constructed and attached in such
a manner as to prevent employee contact with live circuitry
capable of causing human injury. Such guards must be of durable
construction, adequate to prevent injurious contact, and
remain in place at all times that the equipment is energized.
|